Question 13/29
A proprietary field-glued mass timber beam splice will require which of the following:
Correct Answer: A
A proprietary field-glued mass timber beam splice requires special inspection because the connection relies on a field-applied adhesive process that is not covered as a routine prescriptive mass timber connection in Table
1705.5.3. The controlling mechanism is IBC Section 1705.1.1, which authorizes the building official to require special inspection for unusual materials, systems, or installation procedures, particularly where compliance depends on additional manufacturer installation instructions.
The ICC code-development rationale for the tall mass timber provisions specifically identifies field-glued mass timber beam or panel splices as an example of work for which special inspection can be required.
Inspection must address the approved evaluation report and manufacturer's instructions, including substrate preparation, moisture and temperature limits, adhesive storage and expiration, mixing or proportioning, application quantity, open time, member alignment, clamping or pressure, and curing conditions.
Approval by the permit applicant has no regulatory significance. Verification by the registered design professional may supplement the inspection program but does not replace the approved special inspector. A building official may observe the work, but routine field verification by that official is not the prescribed quality-control procedure.
References/Topics: 2021 IBC Sections 1704.2, 1704.3 and 1705.1.1; special cases; proprietary field-glued mass timber splices.
1705.5.3. The controlling mechanism is IBC Section 1705.1.1, which authorizes the building official to require special inspection for unusual materials, systems, or installation procedures, particularly where compliance depends on additional manufacturer installation instructions.
The ICC code-development rationale for the tall mass timber provisions specifically identifies field-glued mass timber beam or panel splices as an example of work for which special inspection can be required.
Inspection must address the approved evaluation report and manufacturer's instructions, including substrate preparation, moisture and temperature limits, adhesive storage and expiration, mixing or proportioning, application quantity, open time, member alignment, clamping or pressure, and curing conditions.
Approval by the permit applicant has no regulatory significance. Verification by the registered design professional may supplement the inspection program but does not replace the approved special inspector. A building official may observe the work, but routine field verification by that official is not the prescribed quality-control procedure.
References/Topics: 2021 IBC Sections 1704.2, 1704.3 and 1705.1.1; special cases; proprietary field-glued mass timber splices.
Add Comments
- Other Question (29q)
- Q1. Regarding water supply for the protection of buildings under construction, when combustibl...
- Q2. Periodic special inspection of sealants or adhesives as specified by the International Bui...
- Q3. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q4. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q5. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q6. In mass timber construction of Type IV-C, the fire-resistance ratings of bearing walls are...
- Q7. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q8. Disregarding footnotes, which of the following is true regarding fire-resistance ratings o...
- Q9. Calculated mass timber fire resistance can include each of the following except:...
- Q10. Sealants used to resist passage of air in construction Type IV-A, shall be in accordance w...
- Q11. Which of the following best describes circumstances for which a separate inspection by a b...
- Q12. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q13. A proprietary field-glued mass timber beam splice will require which of the following:...
- Q14. For Type IV-A construction, noncombustible protection shall provide what fraction of the r...
- Q15. Mass timber is allowed in which of the following International Building Code Construction ...
- Q16. Based on the definition of cross-laminated timber (CLT), panels are manufactured as follow...
- Q17. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) If the glulam beam...
- Q18. The maximum allowable height for a Group E building of Type IV-A construction with an auto...
- Q19. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) The exterior wall s...
- Q20. According to UL Fire Resistance Directory, a "finish rating" is the time:...
- Q21. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q22. Periodic special inspection of sealants or adhesives shall be conducted where sealants or ...
- Q23. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q24. For Type IV-A, IV-B, and IV-C construction, each of the following materials on the exterio...
- Q25. Which of the following provisions for mass timber used for interior exit and elevator hois...
- Q26. The fire-resistance of a protected mass timber assembly is equivalent to the fire resistan...
- Q27. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q28. Adhesives used to resist passage of air in construction Type IV-C, shall be in accordance ...
- Q29. Which of the following provisions for mass timber used for interior exit and elevator hois...
[×]
Download PDF File
Enter your email address to download InternationalCodeCouncil.93-Tall-Mass-Timber-Buildings.v2026-11-23.q29.pdf