Regarding water supply for the protection of buildings under construction, when combustible building materials of the building under construction are delivered to a site, the minimum fire flow provided shall be
_____ gpm.
_____ gpm.
Correct Answer: C
The required minimum fire flow is 500 gallons per minute , making option C correct.
2021 IFC Section 3313.1 requires an approved temporary or permanent water supply for fire protection to become available at specified stages of construction, including when combustible building materials arrive on the site. Section 3313.2 then establishes the specific requirement: when combustible building materials for the building under construction are delivered, a minimum fire flow of 500 gpm must be provided.
The hydrant supplying this flow must be located within 500 feet of the combustible building materials as measured along an approved fire apparatus access lane. If a single hydrant cannot provide the required coverage because of site configuration, additional hydrants are required.
The 500-gpm value in this question is the construction-stage minimum associated with combustible-material delivery. It should not be mistaken for the final required fire flow of the completed building. Depending on construction type, fire separation distance, building area, and subsequent phases of vertical construction, the required available water supply can be greater.
For mass timber projects, verifying this water supply before large timber packages arrive is a critical construction-phase fire-safety control.
References/Topics: 2021 IFC Sections 3313.1 and 3313.2; combustible building materials; minimum construction fire flow.
2021 IFC Section 3313.1 requires an approved temporary or permanent water supply for fire protection to become available at specified stages of construction, including when combustible building materials arrive on the site. Section 3313.2 then establishes the specific requirement: when combustible building materials for the building under construction are delivered, a minimum fire flow of 500 gpm must be provided.
The hydrant supplying this flow must be located within 500 feet of the combustible building materials as measured along an approved fire apparatus access lane. If a single hydrant cannot provide the required coverage because of site configuration, additional hydrants are required.
The 500-gpm value in this question is the construction-stage minimum associated with combustible-material delivery. It should not be mistaken for the final required fire flow of the completed building. Depending on construction type, fire separation distance, building area, and subsequent phases of vertical construction, the required available water supply can be greater.
For mass timber projects, verifying this water supply before large timber packages arrive is a critical construction-phase fire-safety control.
References/Topics: 2021 IFC Sections 3313.1 and 3313.2; combustible building materials; minimum construction fire flow.
Add Comments
- Other Question (29q)
- Q1. Regarding water supply for the protection of buildings under construction, when combustibl...
- Q2. Periodic special inspection of sealants or adhesives as specified by the International Bui...
- Q3. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q4. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q5. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q6. In mass timber construction of Type IV-C, the fire-resistance ratings of bearing walls are...
- Q7. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q8. Disregarding footnotes, which of the following is true regarding fire-resistance ratings o...
- Q9. Calculated mass timber fire resistance can include each of the following except:...
- Q10. Sealants used to resist passage of air in construction Type IV-A, shall be in accordance w...
- Q11. Which of the following best describes circumstances for which a separate inspection by a b...
- Q12. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q13. A proprietary field-glued mass timber beam splice will require which of the following:...
- Q14. For Type IV-A construction, noncombustible protection shall provide what fraction of the r...
- Q15. Mass timber is allowed in which of the following International Building Code Construction ...
- Q16. Based on the definition of cross-laminated timber (CLT), panels are manufactured as follow...
- Q17. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) If the glulam beam...
- Q18. The maximum allowable height for a Group E building of Type IV-A construction with an auto...
- Q19. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) The exterior wall s...
- Q20. According to UL Fire Resistance Directory, a "finish rating" is the time:...
- Q21. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q22. Periodic special inspection of sealants or adhesives shall be conducted where sealants or ...
- Q23. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q24. For Type IV-A, IV-B, and IV-C construction, each of the following materials on the exterio...
- Q25. Which of the following provisions for mass timber used for interior exit and elevator hois...
- Q26. The fire-resistance of a protected mass timber assembly is equivalent to the fire resistan...
- Q27. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q28. Adhesives used to resist passage of air in construction Type IV-C, shall be in accordance ...
- Q29. Which of the following provisions for mass timber used for interior exit and elevator hois...
[×]
Download PDF File
Enter your email address to download InternationalCodeCouncil.93-Tall-Mass-Timber-Buildings.v2026-11-23.q29.pdf