Question 9/29
Calculated mass timber fire resistance can include each of the following except:
Correct Answer: A
Minimum prescriptive dimensions are not themselves a component added into a calculated fire-resistance time. Therefore, option A is the exception.
IBC Section 602.4 states that a mass timber element's required fire resistance can be based on the fire- resistance contribution of the mass timber, the noncombustible protection, or a combination of those two components. Options B, C, and D reflect those permitted approaches.
Minimum dimensions under Section 2304.11 serve a different function. They establish the minimum cross- sectional size and construction characteristics required for qualifying heavy timber or mass timber elements.
A member can satisfy the minimum dimensional requirement without automatically achieving every required one-, two-, or three-hour fire-resistance rating. The structural fire calculation must evaluate the remaining effective section after charring, elevated-temperature effects, applied loading, and any credited protective materials.
The inspector must therefore verify both requirements independently: the installed member must meet the minimum code dimensions and must match the approved fire-resistance design. Increasing a member to the minimum prescriptive size does not by itself replace the required calculation, tested assembly, or approved protection system.
References/Topics: 2021 IBC Sections 602.4, 703.2, 722.7 and 2304.11; calculated mass timber fire resistance.
IBC Section 602.4 states that a mass timber element's required fire resistance can be based on the fire- resistance contribution of the mass timber, the noncombustible protection, or a combination of those two components. Options B, C, and D reflect those permitted approaches.
Minimum dimensions under Section 2304.11 serve a different function. They establish the minimum cross- sectional size and construction characteristics required for qualifying heavy timber or mass timber elements.
A member can satisfy the minimum dimensional requirement without automatically achieving every required one-, two-, or three-hour fire-resistance rating. The structural fire calculation must evaluate the remaining effective section after charring, elevated-temperature effects, applied loading, and any credited protective materials.
The inspector must therefore verify both requirements independently: the installed member must meet the minimum code dimensions and must match the approved fire-resistance design. Increasing a member to the minimum prescriptive size does not by itself replace the required calculation, tested assembly, or approved protection system.
References/Topics: 2021 IBC Sections 602.4, 703.2, 722.7 and 2304.11; calculated mass timber fire resistance.
Add Comments
- Other Question (29q)
- Q1. Regarding water supply for the protection of buildings under construction, when combustibl...
- Q2. Periodic special inspection of sealants or adhesives as specified by the International Bui...
- Q3. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q4. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q5. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) In Type IV-B constr...
- Q6. In mass timber construction of Type IV-C, the fire-resistance ratings of bearing walls are...
- Q7. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q8. Disregarding footnotes, which of the following is true regarding fire-resistance ratings o...
- Q9. Calculated mass timber fire resistance can include each of the following except:...
- Q10. Sealants used to resist passage of air in construction Type IV-A, shall be in accordance w...
- Q11. Which of the following best describes circumstances for which a separate inspection by a b...
- Q12. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q13. A proprietary field-glued mass timber beam splice will require which of the following:...
- Q14. For Type IV-A construction, noncombustible protection shall provide what fraction of the r...
- Q15. Mass timber is allowed in which of the following International Building Code Construction ...
- Q16. Based on the definition of cross-laminated timber (CLT), panels are manufactured as follow...
- Q17. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) If the glulam beam...
- Q18. The maximum allowable height for a Group E building of Type IV-A construction with an auto...
- Q19. Refer to the figure by clicking on the EXHIBIT button above. (Exhibit) The exterior wall s...
- Q20. According to UL Fire Resistance Directory, a "finish rating" is the time:...
- Q21. Buildings of Types IV-A, IV-B, and IV-C construction designed to be greater than six stori...
- Q22. Periodic special inspection of sealants or adhesives shall be conducted where sealants or ...
- Q23. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q24. For Type IV-A, IV-B, and IV-C construction, each of the following materials on the exterio...
- Q25. Which of the following provisions for mass timber used for interior exit and elevator hois...
- Q26. The fire-resistance of a protected mass timber assembly is equivalent to the fire resistan...
- Q27. Refer to the exhibit by clicking on the EXHIBIT button above. (Exhibit) In the detail show...
- Q28. Adhesives used to resist passage of air in construction Type IV-C, shall be in accordance ...
- Q29. Which of the following provisions for mass timber used for interior exit and elevator hois...
[×]
Download PDF File
Enter your email address to download InternationalCodeCouncil.93-Tall-Mass-Timber-Buildings.v2026-11-23.q29.pdf